Vacuum on steam radiators

TeeJay
TeeJay Member Posts: 1
We have a situation where the radiators are not getting hot. The 2" supply is hot but where it taps off to the bedroom is slightly warm. We opened up the radiator and feel it pulling a vacuum.  Can this be a partial blockage.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,839
    Look for a sag

    or some other place where water can accumulate in the riser or runout...  that'll do it.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    radiator sucking air

    in addition, if your main vent is plugged up, the radiator vents will be the only vacuum relief available to the system. that could be also the reason those radiators are not heating fully. if the steam arrives just after the thermostat is satisfied, they miss the boat.--nbc
  • DanCanDo
    DanCanDo Member Posts: 15
    TeeJay's Co_Worker

    This place is a huge apartment complex, system piping easily 70 years or older. (2) LARGE Weil McLain Boilers both with 10" Steam headers.  Piping is all jacked up.  The 2" pipe goes directly back to the condensate return, yet is set up as a One Pipe System.  2x3/4 Tee off top of pipe "should" be the steam supply, yet leads to the radiator trap.  The supply side come off the same 2" pipe, Tee on it's side, goes through a"float/ thermostatic" trap and up to the top of the radiator.  YES, this really is how it's piped.

    I followed this pipe all the way back to the boiler room; I seen NO connection to "any" steam supply pipe.  The maintenance company has only been there for the past three years and the problem has been there that long...no records on file either.  Has numerous supply terminations that are flanged off.

    Dan Houlihan...are you there??!!

    There was an error rendering this rich post.

  • Jamie Hall
    Jamie Hall Member Posts: 24,839
    Aren't you guys...

    going to have fun.  Why do I have this feeling that that vacuum radiator may not be the only thing which is a little peculiar, to say the least?



    If you two aren't really familiar with steam, or happy with it, you might want to contact one of the top men on this board -- depending on where you are -- to come around and give a third viewpoint, if only for laughs.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • DanCanDo
    DanCanDo Member Posts: 15
    Jamie...I hear ya

    Jamie, I'm pretty familiar with steam...I tried to walk away, I really did, but I'm told I'm the only one making any kind of sense.  Hoping to hear back from the CZAR Daniel Houlihan.  Location is in Philadelphia, I have a call out to some local vendors looking for a "Senior Citizen" type former tradesman..."just in case" i'm missing something.  The place trully is a MESS though, but I like challenges.

    There was an error rendering this rich post.

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    apartment complex

    maybe you can draw a diagram of this layout. if the piping is 70 years old, it would have been done by the dead men, and probably worked well when first installed.

    maybe it is an old vapor/ vacuum system, and the vacuum was serving a purpose in the days of coal. if so every component would have been designed for low pressure, such as 12 ounces.

    are both boilers firing at the same time, or are they staged? are there motorised valves involved?--nbc
  • DanCanDo
    DanCanDo Member Posts: 15
    NBC...

    I'll visit again to post some good digiatls and do my best to provide a sketch.  There are not motorized dampers, boilers seem to be fired together.  I still can't see how steam gets into this "uninsulated", condensate return, is all it's proving to be. 

    There was an error rendering this rich post.

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    staged firing

    when you get this problem worked out, you may be able to make some additional improvement by way of a staged firing of the boilers. as pressure builds, the lead boiler continues, and the secondary goes off. when it is 20 below, and the condensing load is equal to the firing rate, they would both work.--nbc 