Carlin 301 gas burner reviews
tim smith
Member Posts: 2,898
Frank or anyone else, have any of you used the Carlin gas 301 burner, appx 900 mbh. What do y'all think of it. I am looking at ordering one and wanted your take. Thanks, Tim
Tim I have not installed any
but I was in three schools back a couple of months ago that had three of them operating. We were there doing combustion testing. These had been specified by Carlin and sent from the factory all sized and orificed for the load.
They all performed very well with no real issues they had replaced Beckett oil burners.
There are a lot of options available on the burners and comply with CSD-1 requirements for gas train (check your local requirements)
You can have the factory set up and prewire the burner if you contact Carlin.
There two heads available "B' Head/Tube 400,000 to 700,000 and the "C" Head/Tube 550,000 to 1,100,000.
They can be used on both Natural Gas and Propane.
All three tested in the 80% to 82% range.0 -
nice burner
Just worked on one that was installed improperly. They failed to add a double swing barometric, which is required and did not set the gas pressure's for the btu load of the unit. Needless to say it can and did soot up very badly.
Very simple system over all and tech support was nice to deal with and they did stay on the phone till all number's they recommend were achieved..0
- 87.4K THE MAIN WALL
- 121 Chimneys & Flues
- 15.8K Strictly Steam
