Rising water level
tsb
Member Posts: 5
I'm having an issue with a rising boiler water level. The system does not have an automatic water feeder or domestic hot water coil. The condensate seems to return quickly from the returns. I flushed the boiler on Sunday when it was cold (off for 3 hours) and filled to the normal water level. Today the water level is about 1/4" higher than normal.
I'm thinking that the water intake ball valve has a very slight leak. Does this assessment make sense?
I'm thinking that the water intake ball valve has a very slight leak. Does this assessment make sense?
0
Comments
-
Leak
Hi - The valve supplying the boiler with makeup water to the boiler is one possibility and if you have a coil installed in your boiler for domestic hot water then a pinhole leak in the coil is another possibility.
- Rod0 -
Leak
No hot water coil, so I guess that it is probably the valve. The valve is only about 6 years old (replaced when the boiler was replaced).
Any other more obscure possibilities before I replace the valve?
Thanks.0 -
Closed radiator valves
Do you have any radiators turned off by the radiator valve? Sometimes a radiator will fill up with condensate and begin to drain back.
MC0 -
One
One of four radiators on the second floor is closed, but it was closed last heating season and this problem did not exist. Should I rotate this radiator air vent rather than having the valve closed?0 -
Extra Water
Opening the valve and rotating the vent to shut the radiator off would be worth trying. At least that way you know the radiator isn't storing water and causing your problem. It's pretty easy for these old valves to leak steam into the radiator where it condenses and a lot harder (slower) for the water to leak back out. If you're shutting down the radiator for a long period of time then you might consider replacing the vent with a brass pipe plug.
- Rod0 -
Air vent
yes, the radiator should be turned off by rotating the air vent, rather than closing the valve. But it is unlikely that the closed valve is the cause of the water level problem -- have to be a pretty fair amount of water hung up in the radiator to do that.
I'd bet on the water level problem coming from the feed valve. Use a quality quarter turn ball valve as the replacement.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements