Can one overvent the main?
acl10
Member Posts: 349
Can one overvent the main? Would that cause to much water to return to the boiler to quickly?
0
Comments
-
I don't see how...
the whole idea of the thing is to get steam throughout the length of the main as quickly as possible. Consider that some very old systems -- before reliable vents appeared on the scene -- vented through an open condenser (big radiator) and on into the chimney through another open pipe!
The only way this could lead to a return water problem would be if you had a lot of main and it wasn't insulated; even then, I can't see that it would be a problem. And your mains are insulated, aren't they?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Main venting
You can't overvent a main but you can overvent the radiators. A very high venting rate on a radiator can cause the steam to condense and return at a high rate.
Also uninsulated pipes in the basement can lead to a lot of condensate. Insulate everything you can it the basement. And remember the old maxim - vent your mains quickly and your radiators slowly.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements