Buderus G115 / Rello F5 - frequent relight
Jbresee
Member Posts: 1
in Oil Heating
Hi,
I've got an intermittent problem with the burner lighting, running a couple of seconds, and re-lighting. As a part of the annual cleaning, I replaced the filter, screen and nozzle, cleaned the CAD eye, and bled the line.
The restarts don't trip the burner reset.
My thinking is that I've got an issue with either pump pressure (pump failure) or something restricting oil flow (gunk in the bottom of the tank). I have to run out an pick up an adapter for my gauge to test the pump pressure.
Do you guys have any other thoughts on this? Obviously, I'm new to the Riello.
Thanks,
Jim
I've got an intermittent problem with the burner lighting, running a couple of seconds, and re-lighting. As a part of the annual cleaning, I replaced the filter, screen and nozzle, cleaned the CAD eye, and bled the line.
The restarts don't trip the burner reset.
My thinking is that I've got an issue with either pump pressure (pump failure) or something restricting oil flow (gunk in the bottom of the tank). I have to run out an pick up an adapter for my gauge to test the pump pressure.
Do you guys have any other thoughts on this? Obviously, I'm new to the Riello.
Thanks,
Jim
0
Comments
-
the riello burner
rarely goes bad,i won't just check the pump psi just yet.you probaly need to bleed it better the riello is very tricky. i reccomend a pro.i also reccomend to be gentle with it when you work on it.0 -
Thanks!
Thanks for the feedback!
A flakey reading from the CAD cell or air in the line both make a lot of sense.
I will re-bleed the lines and really clean the area around the nozzle and see if that clears up the frequent re-lighting issues.
Thanks again for the replies.
Jim0 -
if you have
2 oil lines more than likely you do not have air in the lines.more than likely i would check all the contact under the primary control.sometimes when you remove the primary control on this burner the contacts get bended when you want to have them all lined up before you slide the control back in.0 -
I have seen this before.
Check the Oil Valve solenoid. If the coil is not all the way seated, the valve stem "floats" causing intermittent oil delivery.
Not saying that this is whats happening, but more likely that a pump problem. Those burners are bullet proof.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements