Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
WM 1013-200

harry2
Member Posts: 1
I just replaced the Integrated Boiler Control on a WM GV4 Series 1 to the new updated 1013-200. Upon powering up, the power light and the tstat/circulator light come on and that is as far as it goes. I have tested the limit switches and they are closing like they should. Any ideas are appreciated as it is getting really cold here.
0
Comments
-
new control
page 51 -- 2nd light means circulator and blower on. Does the blower come on? Is the circulator on? Give us some more details.
limit switches and block switch contacts closed - are for the third light.
The manual below, I believe, is the operation sequence:
http://www.weil-mclain.com/en/multimedia-library/pdf/weil-mclain-pdf/products/boilers/gas-boilers/gv/gv_boiler_manual.pdf0 -
In that same manual
starting on page 66 and in particular page 70 you will find troubleszhooting procedures.0
This discussion has been closed.
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 971 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements