Carrier 58GP, GS gas furnace IID pilot
Del
Member Posts: 52
in Gas Heating
Tim, I've got a number of questions about the t-stat terminals on this unit. There are R, Gh, W, Gc, Y and C. #1) There is a jumper between R and Gh. On the diagram, it looks like the Gh terminal is connected right to the heating fan relay. Since there is a jumper R-Gh, would that cause continuous low speed fan operation? What is the point of the jumper? If i was hooking up a typical T-stat for heating, would t-stat R go to this Gh terminal instead of R? It looks like during heating operation, the fan relay is energized through the gas valve and a time delay. Does Gh have something to do with continuous fan operation when t-stat is in heat mode, or is it used as 24V for heating instead of R? Where would my G from the t-stat go?
#2) It looks like the Gc terminal controls the Cooling fan relay, but it doesn't look like Y is controlling anything. Do I need a jumper between Y and Gc in order to control the condenser and the fan relay through the Y terminal of the T stat?
What would a typical RC, RH, G, C, W and Y thermostat hookup look like with this furnace for heating/cooling and fan control on or auto? Thanks for your time!
-Mike
<a href="http://www.xpedio.carrier.com/idc/groups/public/documents/.../58gp,gs-2si.pdf">www.xpedio.carrier.com/idc/groups/public/documents/.../58gp,gs-2si.pdf</a>
#2) It looks like the Gc terminal controls the Cooling fan relay, but it doesn't look like Y is controlling anything. Do I need a jumper between Y and Gc in order to control the condenser and the fan relay through the Y terminal of the T stat?
What would a typical RC, RH, G, C, W and Y thermostat hookup look like with this furnace for heating/cooling and fan control on or auto? Thanks for your time!
-Mike
<a href="http://www.xpedio.carrier.com/idc/groups/public/documents/.../58gp,gs-2si.pdf">www.xpedio.carrier.com/idc/groups/public/documents/.../58gp,gs-2si.pdf</a>
0
Comments
-
Mike is this
a new system or has it been running? What is the make and model number of the thermostat? Is the thermostat wired to a control board, if so give me some numbers and make?0 -
Older system
Tim- this is an older system I went to service. The customer is a restaurant, and she had some handyman put in a new thermostat. I don't remember the brand, but it had the typical battery powered Rh, Rc, W, G, Y. It is hooked right to the unit PCB, and I put in a link to the wiring diagram in my first post. When I got there the unit was running the fan and not igniting, so I pulled the t stat wires off the unit, put in a call for heat and it worked fine.Started tracing the thermostat wires, and found a birdnest of sloppy splices with all different color wires, it was basically impossible to tell which color was which, so it being the middle of brunch hour, I wire nutted two wires at the thermostat, then went down to the unit and checked which were connected, and hooked those up to R-W at unit and thermostat and it worked fine. I told her I'd come back during regular business hours and pull new wire and hook it up so the ac would work next summer! I was looking over the diagram, and due to the Gh Gc terminals, jumper on R--Gh, I wasn't sure how to go about wiring it up, especially since they like to keep the fan on. I mean, I could take the thermostat down to the unit and figure it out, but I figured I'd ask here first ; ). Thanks again.0 -
Ok, so
I went back to this job and ran new thermostat wire from the thermostat to the unit. Had 24V at R and Gh. When I jumped R---Y, the fan did not turn on for the A/C, I had to jump R-Gc for that to happen, so I put a yellow jumper between Gc and Y to kick the condenser on, and things are working OK. For the heat, I just used the typical R-W thermostat connections. Heat and A/C now function normally. The only thing I wasn't sure about was where to hook the G from the thermostat so they can have fan only operation. Should I cut the jumper(part of the circuit board) between R and Gh? I wonder why they designed the terminals this way? Shouldn't there be a separate terminal to switch fan relay? From the diagram, Gh appears to be it, but for some reason it is jumped to R.
Anyone have any ideas? Thanks.
-Mike0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements