Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

outdoor reset

drhvac
drhvac Member Posts: 190
I have a Teckmar outdoor reset on my own boiler. I notice most of the time, the water temp is set at 140 degrees. My concern is with a conventional boiler with a supply temp of 140, my return temp is going to be around 120. This is kind of cool for a conventional boiler, which cause condensation problems. How do I rectify this? Or is this a problem at all?

Comments

  • Ironman
    Ironman Member Posts: 7,529
    Adjust The Curve

    Adjust the reset curve so that your baseline temp is 140 deg. It will be a pretty flat line curve.



    Also, consult the manufactuer for the minmum recommended temp.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
This discussion has been closed.