testing a dc pilot sensor
Jim Wy.
Member Posts: 43
I am working on a steam boiler w/ a standing pilot that has a thermocouple for the pilot valve and a flame sensor to prove pilot flame for the main valve. I cleaned the sensor and dont see any cracks in the ceramic yet the reset button needs to be pushed every day. Does anyone know how to test the flame sensor ?
0
Comments
-
If that's a flame-rectification system
you need a micro-ammeter to measure the current flowing thru it.
But often, these nuisance lockouts are the result of a bad ground. I often run a bare ground wire from the pilot bracket to the spark module ground connection. This bypasses the boiler chassis which sometimes doesn't ground as well as it should.
And of course, the electrical circuit feeding the boiler should be well grounded.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Jim Wy what kind of
system is this, I am assuming it is a commercial boiler system? Is that correct? Give us some control numbers so we can give you correct information.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements