Modulating Honeywell pressuretrol without a differential?
KnowNothing
Member Posts: 1
I was recently at a building with this pressuretrol set up. It appears that the one that I have enlarged is the modulating pressuretrol due to the bellows at the base. However, I can't understand how there is a modulating range, when it looks like there is just one setting (2.5 psi). I can't find any literature that says what the default differential is, or if it is additive or subtractive. Does anyone have any suggestions on how this is working? I'm recommending that the owner replace the control to allow for proper setting, but I'd like to have a sense of how the system is operating currently. Thanks in advance!
0
Comments
-
What are the control
numbers?0 -
L91A modulating pressure control
You are looking at a Honeywell L91A series modulating pressure controller. This controller may drive a firing rate motor on the burner. This control will not have a differential as this term is used for a digital switch. We call it a proportional band or throttling range. Some of the models have the feature of adjustment and some do not. Please refer to [u][color=#0000ff]www.customer.honeywell.com[/color][/u] and type in the search located to the left of the page L91. I am enclosing a link to the “Product Data for you use.
[u][size=12][color=#800080]http://customer.honeywell.com/techlit/pdf/PackedLit/60-2152.pdf[/color][/size][/u]0 -
L91 range
Thanks GBriggs. If there is no differential, then what are the high and low limits for the firing rate motor? It seems like the non-adjustable throttling range at mid-scale on the L91 is 0.5 psi. If the main scale is set at 3 for example, would the high and low be 3.5 and 2.5 respectively? It seems limiting, but I can at least see how it would work if that were the case.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements