Triple aquastat relay question

Joseph_4
Joseph_4 Member Posts: 293
I have a customer with limited funds, who has a 120 volt aquastat relay (L8124E). Can I use it for a 24 volt system using a stepdown transformer?

Comments

  • Joseph_4
    Joseph_4 Member Posts: 293
    I meant a L8124A

    I typed the question by accident with wrong letter. I meant a L8124A aquastat which normally provides 120 v at b1 1nd b2
  • Tim McElwain
    Tim McElwain Member Posts: 4,642
    Answered by e-mail

    yes B1 and B2 can power the primary side of the trnasformer to give 24 volts on the secondary of a tep down transformer,