Triple aquastat relay question
Joseph_4
Member Posts: 296
I have a customer with limited funds, who has a 120 volt aquastat relay (L8124E). Can I use it for a 24 volt system using a stepdown transformer?
0
Comments
-
I meant a L8124A
I typed the question by accident with wrong letter. I meant a L8124A aquastat which normally provides 120 v at b1 1nd b20 -
Answered by e-mail
yes B1 and B2 can power the primary side of the trnasformer to give 24 volts on the secondary of a tep down transformer,0
This discussion has been closed.