Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Triple aquastat relay question
Joseph_4
Member Posts: 293
I have a customer with limited funds, who has a 120 volt aquastat relay (L8124E). Can I use it for a 24 volt system using a stepdown transformer?
0
Comments
-
I meant a L8124A
I typed the question by accident with wrong letter. I meant a L8124A aquastat which normally provides 120 v at b1 1nd b20 -
Answered by e-mail
yes B1 and B2 can power the primary side of the trnasformer to give 24 volts on the secondary of a tep down transformer,0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements