An interesting observation
Jamie Hall
Member Posts: 24,496
which might be of some value to someone. I hope.
I recently had a lovely new boiler installed -- really nice job and first class workmanship (thanks, Charles!). Runs much better than the old one, which was the same boiler but the old near boiler piping was a bit odd... (not to mention the boiler hadn't been assembled properly and finally developed a neat hole above the water line).
However, I have improved things even further. The system is Hoffman Equipped, and really doesn't like anything over about 7.5 ounces per square inch. That said, vapourstats tend to be a bit twitchy at those low pressures. I put a snubber on the pigtail to the vapourstat and it made quite a difference -- no more tendency for false trips on small pressure surges (which are inevitable). They're cheap. Highly recommended. System is now set at 7.2 ounces cut out, 6.7 ounce differential.
For what it's worth...
I recently had a lovely new boiler installed -- really nice job and first class workmanship (thanks, Charles!). Runs much better than the old one, which was the same boiler but the old near boiler piping was a bit odd... (not to mention the boiler hadn't been assembled properly and finally developed a neat hole above the water line).
However, I have improved things even further. The system is Hoffman Equipped, and really doesn't like anything over about 7.5 ounces per square inch. That said, vapourstats tend to be a bit twitchy at those low pressures. I put a snubber on the pigtail to the vapourstat and it made quite a difference -- no more tendency for false trips on small pressure surges (which are inevitable). They're cheap. Highly recommended. System is now set at 7.2 ounces cut out, 6.7 ounce differential.
For what it's worth...
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
0
Comments
-
i ordered mine yesterday ...
i tried to find one locally .. after talking to the lovely folks in North Carolina (OMS), they directed me to their distributor in Rochester, NY (Tel-Tru) .. they directed me to a place in Brooklyn .. but the place in Brooklyn needed a $50 order min, and wanted me to wait 2 weeks to get the items. I'm not even mentioning their name ..
You can get them from Tel-Tru directly, but gaugestore.com is better equipped and the pricing is within $1 including shipping.
I'm interested to see the difference ..1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements