monoflow question
jonny88
Member Posts: 1,139
i work with the so called best when it comes to heating,,however after reading dans books i have learned a lot of the things i have been taughT are wrong,bull head tees on steam,cut in 3 cut out 5 etc.i have a question regarding monoflow tees,first of all are diverter tees the same as a monoflow tee.the tee we use has a diverter in it which looks like it should direct water into the radiator.dan however says they should go on the return side.i would really appreciate some help.thanks in advance
0
Comments
-
Monoflow/Diverter Tees:
Most monoflow tees available today have a nozzle/orifice inside. They also usually have a groove around the side of the tee, on one side of the branch outlet. They may have arrows incised on the side. The arrows always point to the direction of the flow when used on the inlet or outlet. If you use two monoflows, the grooves face each other. If you use one, it is usually put on the return side of the loop. If you put it on the supply side, the restriction causes a portion of the water to take the path of least resistance. On the return, the venturi causes a vacuum and "pulls" the water through the emitter loop.
Hope that is clear. Not having one in hand, I'm going from memory.
I use them often when I am looping fin tube baseboard and need to put a toe kick heater in the loop. If you use a monoflow tee setup, there isn't a reduction in flow and pressure through the coil. I've seen coils hooked up direct. It really screws up a good loop.0 -
thanks for your help iceman
thanks for your help.my first time here.i work with two licensed plumbers in nyc and they swear that the monoflow tee goes on the feed then we put a regular tee about 4 inches after it,i am really starting to question their knowledge,hard to teach an old dog new tricks,thanks again0 -
thanks for your help iceman
thanks for your help.my first time here.i work with two licensed plumbers in nyc and they swear that the monoflow tee goes on the feed then we put a regular tee about 4 inches after it,i am really starting to question their knowledge,hard to teach an old dog new tricks,thanks again0 -
Mono flow tees...
Work somewhat better on the return side. The distance between the tees should be greater than the width of the radiator. 4 inches of separation would only work on a 4inch rad. Never seen one.
Are they confusing these with primary/secondary tees that must be closely spaced?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
mono flow tees
nothing to do with primary/secondary piping,their notion is you have a loop,as water comes to the first rad,it will go through the monoflow tee,the scoop in the tee will lift water up into the rad,and come out the regular tee and continue on the loop.it seems to work but i dont know how well it works,we always have problems bleeding rads0 -
ahh
You have to watch the mono T mfr. If it's a venturi with the cone inside, it goes on the return, cone going with flow. If the rad is lower than the main, you have to use mono T's on both S/R.
If it's an Asian cast scoop type T, it's gotta go on the supply with the scoop curving up into the branch. In a less than stellar moment some years ago, I tried to defy physics, being so used to the tried and true B+G monoflo's.0 -
that clears it up
the tee we use is the one with the scoop,thankyou for clearing that up for me mr.bona.in dans book he says on diverter tee systems the diverter tee goes on the return.that really threw me for a loop.in the future i will look out for the conical tee.unfortunatly our supply house has recently gotten real chep with the quality of there material.its hard to by american fittings and compete with the people using chinese materials,anyway thats another story,thanks again for your time0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements