Theoretical Boiler Meltdown?
TomM
Posts: 233
I'm trying to figure out (theoretically) what would happen if the low water cutoff on my boiler failed, all the water boiled out or was lost, and the burner stayed on, for an infinite amount of time (say, if I was away for a weekend).
-
The melting point of cast iron is 2150F to 2360F according to some random engineering website. I understand that in the above situation, the boiler would definitely crack, but would the cast iron actually melt? Would it actually cause a housefire, or would it sit there and fire at an empty cracked boiler until I came home?
-
How do you prove this either way, thermodynamicallywise?
-
Or, better yet, anybody have pics?
-
The melting point of cast iron is 2150F to 2360F according to some random engineering website. I understand that in the above situation, the boiler would definitely crack, but would the cast iron actually melt? Would it actually cause a housefire, or would it sit there and fire at an empty cracked boiler until I came home?
-
How do you prove this either way, thermodynamicallywise?
-
Or, better yet, anybody have pics?
There was an error rendering this rich post.
0
Comments
-
You might wish to ask
You might wish to ask what would happen if someone were to notice the lack of water, and turn it on. Or if it shut off and water in the system ran back into the boiler.0 -
my guess is
the burner would fail before meltdown.0 -
meltdown
This is the result of a run away Smith Pac:-) I always forget to take before pictures. The old boiler ran for well over 12 hours before the FD was called. They shut it down. LWCO never dropped and the feed never came on. The boiler cracked, but now melt down. I think I am going to have to lower those returns.
Peace
Matthew0 -
I was thinking of this.
http://www.heatinghelp.com/article/11/Hot-Tech-Tips/203/Low-water-cutoffs-belong-on-ALL-boilers0 -
That is a good link. Should have 2 LWCO on all boilers,
Two automatice water feeders as well and alarms when stuff isn't up to snuff.
Maybe another $300 if all done at factory. Kind of like air bags.0 -
belt and braces with your pants, sir?
Not sure what the codes say, but...
Every boiler should have two LWCOs, one of which is manual reset. The upper, automatic one can be tied into an automatic water feeder, if you like. And if you keep track of how much water it feeds.
Every steam boiler should have at least two pressuretrols. One of them might be a vapourstat, but the other should be set to something sane -- like 5 psi -- and again be a manual reset.
And a gauge glass, with blowdown taps.
And there is no substitute for looking at the dad-burned thing once in a while...
Just one man's thoughts...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements