Emergency on/off boiler switch...
john p_2
Member Posts: 367
Would like to mount the on/off switch on a panel to which I mounted my supply header, zone valve junction boxes and water feed. But have never seen it done any other way than directly to the sheetmetal jacket of the boiler.
0
Comments
-
switch
The reason for jacket mounted switches are for quick easy access while servicing. Whether it be gas or oil, it should be within arm's length from the burner for quick disconnect0 -
Check your local code
John, in Maine it specifies within arms reach while servicing the burner. I am 6'4" with long arms and I asked the question to a state inspector once. He laughed and said, within reach of a normal technician.0 -
Switch
Yes that's a emergency switch for the home owner at a safe distance the one on the unit is a service switch for a quick response and for additional safty while working. A disconnect is better ... Sure your noticing them slowly being added. Like in limit aquastats ..There was an error rendering this rich post.
0 -
Silly rules in Colorado...
The code for commercial buildings requires a fireman's emergency disconnect be mounted just outside of the boiler room door on commercial buildings.
The problem is, in a multi family building, just outside of the boiler room is usually the apartment buildings Laundry room...
Talk about nuisance lockouts.
So, we came to a happy compromise with the AHJ. We would mount the switch, just inside the boiler room door, with a large yellow arrow at the same height that says "EMERGENCY DISCONNECT INSIDE" so that the firemen can reach the disconnect without having to actually walk into the room. That way, the switch is out of reach of mischevious fingers, and is behind a locked door.
I believe the NEC states that if the circuit breaker panel is in the same room as the appliance, that a disconnect is not required. It also states that if the amperage draw of the appliance is less than a certain threshold, that a fused disconnect is not required,,, But the inspectors are so used to seeing them, that we put them in anyway.
Belts with your suspenders sir???
METhere was an error rendering this rich post.
0 -
switch
Emergency switch location always varies, but here in Mass, opening a basement or boiler room door to access an emergency switch will not pass inspection, and must be red cover. I guess it is common sense. Fire or smoke in the basement/boiler room, I don't want to open the door to kill the power0 -
Electrical Tubing connector
Being a servicemen for too many years ... After getting those calls in the middle of the night ... I like to attach a 1/2 conduit clap to the top screw of the switch which spins down and cover the lever .. BX straps work great too if you bend them just right ...
I get a kick out of the standard question of the home owner on those "Switch Off "calls is "Who shut it off ?" Like I snuck in the home to shut the dang thing off and waited outsideThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements