LAARS PROBLEM PROBLEM PROBLEM
FREE
Member Posts: 1
Hello, I have a Laars EBP about 5 years old, The boiler constantly cycles and rarely shuts off. Even when no call for water ! It shakes and rumbles the pipes and then reads F-4. Then it just starts up again and cycles. My water is hot but there is something definitely wrong with this design. Over years Ive had control panel changed, igniter and one flow sensor....Should I just get rids of this unit?
0
Comments
-
Have you
contacted Laars and what did they say?"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
F-4 Code...
Means supply sensor error. Two things to check:
1. From what you describe, it sounds like no water circulation thru the boiler. Look for a bad circ. pump or valve closed. It's also possible that the heat exchanger needs de-scaling. Is there sufficient water pressure on the boiler? should be 12psi min.
2. The sensor itself could be bad. Should measure 10k ohms @ 77deg.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements