160F as a design temerature with standard efficiency boiler
Vad
Member Posts: 55
Is this acceptable to use 160F as a design temperature with Standard efficiency boiler that have 140F as minimum return temperature (Burnham Series 2)? Setting 160F on Standard efficiency boiler will I get more energy efficient system?
I am thinking on using ModCon boiler but still there is a chance that I will be using standard efficiency one. I need to calculate baseboard size and install it prior to selecting the boiler. I realize that it is not the really right way of building the system.
If I understand right, it make sence to make the design temperature 160F for use with high efficiency boiler.
I appreciate you input.
Thank you,
Vad
I am thinking on using ModCon boiler but still there is a chance that I will be using standard efficiency one. I need to calculate baseboard size and install it prior to selecting the boiler. I realize that it is not the really right way of building the system.
If I understand right, it make sence to make the design temperature 160F for use with high efficiency boiler.
I appreciate you input.
Thank you,
Vad
0
Comments
-
Here's why
A boiler running on outdoor reset will only reach its design temperature a very small portion of the heating season. If that design temperature is outside of the condensing range (160) then you wouldn't reap the benefits that a mod-con boiler provides during that small portion of the heating season, but that's OK, because you'd still be reaping the benefits during the bulk of the heating season.
Using 160 as your design supply temperature allows you to size your emitters (radiators or baseboard) smaller than if you were using, say, 120 as your design supply temperature. This saves money up front, and doesn't give up much in the way of fuel savings. Beyond that, there are diminishing returns.
A non-condensing boiler may be theoretically a teensy bit more efficient with lower supply temperatures, but this is negligible and it definitely doesn't ever result in payback on the extra cost you spent on your emitters to bring the design temperature lower. Stop mincing already and go for condensing. :-)0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements