Pigtail orientation?
mike m_3
Member Posts: 10
Before I install this new pigtail atop the LWCO are there guidelines as to proper height with regard to the boiler water line ? Seems to me that the center of pigtail should be above the water line,if so how much? Also,any rules as to whether the pigtail should be placed vertically or horizontally? In line with LWCO or perpendicular? Thanks
Pigtails
Hi Mike-
Within reason, the higher about the waterline the better. The idea is to get the gauge and /or pressuretrol controls away from boiling water/live steam that could damage them. You can use some pipe fittings (bronze /red brass- available Home Depot) and extend the height up a bit. Place the pigtail at the top. The pigtail should be oriented so you can't see the loop when you face it.(stand in front of the boiler) Some of the older controls were sensitive to being level and so if the loop was set sideways, the thermal expansion of the loop, when it heated up, would tilt the controls.
I've attached a picture of a nice pigtail setup. Referencing the sight glass in the picture, you can see the pigtail/gauges are well above the boiler's waterline. Don't worry about filling the pigtail with water. It will fill adequately on its own with condensate.
- Rod0 -
So thats how you do it!
Thanks Rod, This set up of mine needs a little adjustment.Wish I had ordered a longer pigtail but I will add a short red brass riser to get the pressuretrol and pressure gauge up away from the water line. Thanks for the picture, thats what I was hoping for.
Only thing I'd add
is that yes the pigtail will fill with water -- eventually. Until it does, though, you may find that the pressure (or, if you are using a vapourstat) bounces around a lot (it may bounce a vapourstat enough to make it shut off). Only takes a few seconds to fill... been there...Br. Jamie, osb
- 125 Chimneys & Flues