sizing steam boiler for copper convectors

Options
would  somebody give me a hint how to size replacement steam boiler which would go with copper convectors?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,327
    Options
    A reference

    do you have a reference for the amount of BTU per hour the convectors will produce at 214 F -- steam temperature?  If so, I'd be inclined to do it the same way I would a system with radiators -- add up the demand from the convectors.  Then you could divide by 240 which would give you an equivalent EDR, and go from there.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • and......

    since convectors hold so little heat, you can probably go very light on the Pick up factor, 15 to 20% is probably plenty, if all you piping is insulated or you don't have an unusual system