sizing steam boiler for copper convectors
tonij
Member Posts: 1
would somebody give me a hint how to size replacement steam boiler which would go with copper convectors?
0
Comments
-
A reference
do you have a reference for the amount of BTU per hour the convectors will produce at 214 F -- steam temperature? If so, I'd be inclined to do it the same way I would a system with radiators -- add up the demand from the convectors. Then you could divide by 240 which would give you an equivalent EDR, and go from there.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
and......
since convectors hold so little heat, you can probably go very light on the Pick up factor, 15 to 20% is probably plenty, if all you piping is insulated or you don't have an unusual systemThere was an error rendering this rich post.