low co2 during combustion test
highway
Member Posts: 7
in Oil Heating
Hello all. First post !! Did a tune up on a friends Thermo Dynamics series 110. Replaced the nozzle with same .85 80B. Pump pressure is 140. I have an -02 draft over fire and -04 at the breach. I get a 9 to 10 co2 reading at the breach using a bacarach wet kit tester. I cant seem to get the reading any higher. I have the air almost completely shut. I'm I missing something? Thanks...
0
Comments
-
More info
Is it a Carlin burner in it? If so, what model Carlin. And 110 seems to be a common number for TD. Do you have the exact model number?0 -
Air Leaks
Could also be air leaks dropping the % of CO2 ... Not a great boiler , reading would not alarm me as long a you have a 0 smoke ...There was an error rendering this rich post.
0 -
Draft over fire
If it is a cwl or an ht, you may have to much draft over the fire. The settings for Thermo-Dynamics' boilers our listed on the boiler.0 -
low co2
It has a beckett afg. The boiler calls for a -02 draft over fire, which I have. The chamber liner does have several cracks on the bottom or floor. I have 0 smoke. Thanks for the replies.0 -
wet kit
I would suspect that the fluid needs changing in you tester, as the readings aren't changing. I hope that you did another smoke test, and running a zero smoke. The only poor readings that I've gotten from these are high stack temps, which lowers the efficiency. They are probably the best steel boiler out there other than EK, JMHO. Try a digital tester on it, you may be surprised0 -
low co2
I have a new bacharach wet kit tester with approx 6 tests total. First I checked for smoke and got a zero reading. I then reduced the air and tested again for a trace of smoke. I then checked the co2 reading ( 9 1/2 to 10 ) and then increased the air and tested again for smoke getting a zero smoke reading. I thought it could be the tester, but I checked it on my own boiler when I got home and had a 12 to 13 co2 reading, so I assume the tester is working. My stack temp is 500 *0 -
Leak
Leak between the base and HX,fairly common with drybase boilersTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
that or
the flue collector is not sealed. Pull the burner and fully inspect the chamber, back and sides. Look for heat marks on the jacket midpoint0 -
Correct
Bill is absolutely correct, i assumed that was checked when servicedTo learn more about this professional, click here to visit their ad in Find A Contractor.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements