Sizing Secondary Pump for Replacement Boiler
Mpls_Matt
Member Posts: 2
All,
Obviously I am an amateur for asking such a basic question, but I could really use some help with this.
I've basically settled on the Triangle Tube Prestige Solo 110 to replace my very outdated cast iron boiler. The current system is a single series with cast iron radiators and a Bell & Gosset 3 piece Series HV circulator. The PS110 comes with a Grundfos UPS 15-58F-FC primary pump. How do I size the secondary pump to run the secondary circuit to the cast iron radiators? I have no idea what the system pressure or flow rate of the current system is.
A second question is how do I size the expansion tank if I don't know what the system volume is?
If this helps, the house is roughly 1600 square ft.
thanks for any help,
Matt
Obviously I am an amateur for asking such a basic question, but I could really use some help with this.
I've basically settled on the Triangle Tube Prestige Solo 110 to replace my very outdated cast iron boiler. The current system is a single series with cast iron radiators and a Bell & Gosset 3 piece Series HV circulator. The PS110 comes with a Grundfos UPS 15-58F-FC primary pump. How do I size the secondary pump to run the secondary circuit to the cast iron radiators? I have no idea what the system pressure or flow rate of the current system is.
A second question is how do I size the expansion tank if I don't know what the system volume is?
If this helps, the house is roughly 1600 square ft.
thanks for any help,
Matt
0
Comments
-
Pump Sizing
You don't need a secondary pump if you only have one zone since the large flow will safely pull all the heat out of the boiler's heat exchanger. Use the Grundfos pump; remove the B & G.
What is the size of your supply and return pipes on the boiler? If not larger than 1", use a size 30 expansion tank which is one up from the smallest size, size 15.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Pipe sizes
Alan,
Thanks for the help, I appreciate it. My single circuit is split into two pipe runs that run on each side of the house, prior to the split at the boiler the pipes are 1" 1/4"; but after the pipes split they are 1" from there. So, I'm guessing you're correct with the size 30 tank. The cost to go up to a size 60 tank isn't a lot more; is there a downside to just putting a really large tank in to make sure you have enough volume? Can you have too large of a tank?
Also, any issues with the freeze protection feature if I only use the one circulator? It seems to reference this in the installation manual that you may have issues if you don't have a primary/secondary system. Or is there nothing to worry about here?
Thanks,
Matt0 -
whoa
Are you sure its a true series system? Thats a bad design for CI rads and would be rare.
I seriously doubt the PS110 boiler pump could handle the split, multi tap radiation system that required a HV circ previously
You better get one sized for you, I would help but so much more info is required
Tanks are sized on BTU and SYSTEM VOLUME, guessing the tank size isnt a smart move, but a # 30 would be a good guess.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements