steam returns
johngas
Member Posts: 2
I have a two-pipe system and when i run it some of the returns do not heat up and some do - is this a trap problem and if so which traps are working correctly the returns that are hot or returns that are cold. The radiators do heat up on both situations
0
Comments
-
bad traps?
my guess that some traps have failed open, and are allowing some steam into the returns. the good traps are closing when steam arrives, and therefore the return is cold. probably, new trap insides are available for these, which would make it an easier repair job.--nbc0 -
steam traps
Thanks - the steam traps are Barnes and Jones Thermostatic type which can be replaced fairly easily so I will try it0 -
Testing Steam traps
Home Depot sells a Ryobi Infared thermometer (Model # RP4030) for about $70. "Santa" brought me one last Christmas which I've found is a great help for checking trap function. It has an lazer pointer that you can target on the area where you want to take the temperature. I would hold close (less than a 1 foot away) when taking the temperature as the farther you step back, the larger the area it samples.
- Rod0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements