Tridicator Gauge Failure-Again?

Sorry if this has been covered.  I did a search and couldn't find anything so I figured I'd ask:

When I repiped all my circulators and indirect last Spring I installed a tridicator guage on both the supply and return of my boiler.  One gauge began fogging up immediately after install, the other about 2 weeks later.  I figured oh well, bad batch/too tight/dropped or something so I pulled them and plugged the hole.  Recently I finally changed the boiler and figured now was a good time to replace them.  Different model but same result.  One of the gauges failed immediately (fogged up and didn't register a temperature change) so now it must be me.

I DID NOT over-tighten them,  1/4 turn until they stopped leaking then 1/4 turn more. 

I didn't use tape, only very little dope.

The end of the probe is EXACTLY where it should be, maybe even a little pulled back from the middle of the tee so I know its not bottoming out and damaging the probe. 

What the heck am I doing wrong?

Comments

  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    edited July 2010
    We've been having bad batches of tridicators

    Some register many psi right out of the box . Some have temps off the chart when it should read ambient . These are the ones that come shipped with the boilers we use . I'm assuming they're not the highest quality .



    One thing I found the hard way was not to hand tighten it from the face of the tridicator , it could send the psi side out of whack . Always use a wrench on the shaft .



    A good quality tridicator from a plumbing supply is a good bet . Sorry I don't know brand names though . Hopefully someone will chime in .
  • shoudabeenaplumba
    shoudabeenaplumba Member Posts: 74
    I used a different brand

    I bought them 4 months apart. Installed into a tee with room to spare. Used a wrench and did not over-tighten. What the heck?
  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    I feel your pain .....

    I'm out of spare tridicators to replace the bad ones that come with the boiler ...... It don't happen often , but we replace 2 to 3 boilers a week . If 1 out of 10 are bad and you're waiting for stock or a replacement under warantee .......... 



    The brand that comes with the Weil Mclain seems to be a good gauge . I'll find out who makes it is on Monday and get back to you  .
  • shoudabeenaplumba
    shoudabeenaplumba Member Posts: 74
    Am I doing something wrong?

    Dope on the threads. Is the guage fouling? I could see why that would mess with the pressure/head but not the temp. Also, it wouldn't explain why the gauge is fogging up.
  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    edited July 2010
    I've found them to fog up

    when someone hand threads the gauge all the way . But I've heard one boiler manufacturer in particular ships a gauge that more likely than not will fog up immediately . We use Teflon only and skip the first threads . But you're right , getting sealant in the gauge would only affect the pressure reading .
  • shoudabeenaplumba
    shoudabeenaplumba Member Posts: 74
    I guess I could pick it up with tongs

    move the boiler to a clean room, and use special water.
  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    edited July 2010
    Just trying to help there , buddy

    Of course you have to START threading in the gauge by hand ........



    But if you put too much pressure on the face of the gauge when tightening , funny things can happen to the gauge .



    I wasn't there to see how you installed these tridicators . So I'm going on your word there . Could be you just got unlucky with a bad batch .



    Have a good day and good luck with your endeavour .
  • shoudabeenaplumba
    shoudabeenaplumba Member Posts: 74
    I appreciate the help

    I always lean towards operator error on a listed device.  I could accept it was once but now its twice, being even more carefull the 2nd time.  I'd think it was a bad brand if I hadn't used two different ones.  I'd think it was a bad batch if  I had a dozen of the same lot number of gauge in my truck.

    What's the odds of a failed gauge?  1 in 100?  That makes it about 1 in 100,000.  Time to play the lottery. 
  • hot_rod
    hot_rod Member Posts: 23,191
    tough to find a

    good quality P/T gauge anymore. Even the good old brand names seem to be selling poor quality imports these days.



    Consider a separate pressure and temperature gauge. You can still find quality pressure gauges, I like the fluid filled stainless case versions.



    And you can still find round or vertical, quality temperature gauges. Shop at HVAC supply places.



    Anymore, digital temperature gauges seem to be the most reliable. Either strap on the sensor and insulate over it, or buy a well to go into a tee, and slide the sensor in.



    Strap on thermistior seem to be more accurate than infrared guns, depending on the pipe surface.



    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    One thing I forgot

    And it's a pretty expensive upgrade ..........  a digital aquastat with built in temp readout . I heard one manufacturer will have an all-in-one digital aquastat / LWCO / pressure sensor ( with readout I think )  ..... in the near future .



    Short of that , Hot Rod's idea sounds great .
  • shoudabeenaplumba
    shoudabeenaplumba Member Posts: 74
    I've got the pressure gauge covered

    And all I really wanted was a easy-read temp gauge to tell me how well the supply and return were balanced, and whether I could maybe cut back on the pump speed via motor control ect. 
  • I just use,,

    these,, inexpensive and simple to read.
  • hot_rod
    hot_rod Member Posts: 23,191
    this is what you want

    this dual thermometer from Azel. It reads both temperature and shows the delta T with the push of a button. It has a small battery, good for a year or so, or it can be powered with 24V ac. Reads C or F if that is important. i have installed a bunch, no problems what so ever.



    www.azeltec.com/catalog.0.html.0.html#DIGIT-STAT

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • shoudabeenaplumba
    shoudabeenaplumba Member Posts: 74
    thanks for the link

    That's just what I want.
  • zacmobile
    zacmobile Member Posts: 211
    bad tridicators

    I've run into at least 8 leakers this year, one I replaced and the new one leaked even worse. 2 different brands too, but mostly some no-name ones my local wholesaler carries, for their cost you would think they would be a little more reliable.
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    funny

    this thread pops up, on the day I change my second Buderus tridicator. Stuck on -30.

    I love it how one has to waste at least two hours of their day, no labor re-imbursment, for what the factory dismisses as "just a gauge". So profitable. I laugh when I see the words "instrument" on the box. Too kind. And yes, I am bitter about that. 

    Give us decent gauges!
  • michael_34
    michael_34 Member Posts: 304
    I've been using Wal-rich with no problems...

    knock on wood though! : ) I also used the Caleffi, but it is not as sturdy as the Wal-Rich. My partner drop the Caleffi while still in the box and the pressure indicator never recovered.



    Michael