Combustion analysis
bguthrie
Member Posts: 1
in Gas Heating
Is there any approved or quality method of sealing a drilled hole in PVC for a combustion analysis test on a condensing appliance? I find a lot of them with foil tape, duct tape, and some just left open and this is a positive pressure vent.
0
Comments
-
PVC test hole
I usually drill & tap (for 1/4" NPT), do my analysis, then install a SS solid core pipe plug.0 -
Dave is correct
just add a little RTV high temp sealant to the bolt threads. Our inspectors around here accept that. It is actually best to do it in an elbow ahead of time then just tap the PVC after it is inserted into the elbow and glued.0 -
IPEX's Approved way.
Basically just a bushing & a plug: http://www.ipexinc.com/Content/Products/Product.aspx?IsDownload=true&FileId=1301There was an error rendering this rich post.
0 -
Me too:
I use 1/4" tap. I have a nice tap set that you can purchase almost anywhere. This fitting will never accidentally pop out.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements