I've always been skeptical about the benefits of a hydraulic seperator over primary secondary piping. I understand why you would want to use one over p/s but I don't think the benefits alone are that great. The other selling features of low loss headers is they are supposed to help act as an air removal area, as well as an area for dirt seperation. Well I know the latter 2 features they will do, but not do that well - not well enough to replace a true microbubble resorber or a dedicated dirt seperator (or even better, side stream filter).
So a little research has found these: <a href="http://www.spirotech.nl/_media/en/brochures-producten-en/spirocross_eng.pdf">http://www.spirotech.nl/_media/en/brochures-producten-en/spirocross_eng.pdf</a>
With full air seperation and dirt seperation media for the entire breadth of the low loss header. Does anyone know if they have these available in North America? I know Spirovents sand spirotraps are here but it seems like they are limited selection wise.
These act as a true hydraulic seperator/low loss header, air seperator, and dirt seperator all in one due to the media.
Now I know the Caleffi LLH's have a little screen in them but somehow I like the looks of the above much better....
So a little research has found these: <a href="http://www.spirotech.nl/_media/en/brochures-producten-en/spirocross_eng.pdf">http://www.spirotech.nl/_media/en/brochures-producten-en/spirocross_eng.pdf</a>
With full air seperation and dirt seperation media for the entire breadth of the low loss header. Does anyone know if they have these available in North America? I know Spirovents sand spirotraps are here but it seems like they are limited selection wise.
These act as a true hydraulic seperator/low loss header, air seperator, and dirt seperator all in one due to the media.
Now I know the Caleffi LLH's have a little screen in them but somehow I like the looks of the above much better....
There was an error rendering this rich post.
0
Comments
-
LLH/Microbubble Air Eliminator
Brilliant! I've not seen them yet.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Do you mean a HydroCal?
in sizes 2-6" flanged for now, ASME available also.
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Best Feature
Scott I feel from a design standpoint that the ability to not have temp drops across your zones as multiple zones call as you do with pri/sec is the biggest advantage. The other big feature I like is that the boiler can do it's own thing in keeping it's needed flow rate and you can then play with the flow rates on the system side without having to worry about the boiler side. For instance, adding a Grundfos Alpha on the system side and using the recommended circ pumping threw the boiler in mod/con apps when zoning valves.
I have been using Taco's LLH's on the Viessmann Vitodens 100's as it makes for a nice clean job and is priced right. Have been eliminating the Spirovent and haven't seen any air problems. On the VItodens 200's I have been using Caleffi's as it has a port for a well which I need for the temp sensor. Again eliminating the Spirovent and no problems.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements