condenser, air to water

is it possible to convert an air to air condenser unit to an air to water unit with a suitable brazed plate heat exchanger on the refrigerant line?



has anyone done this?
Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.

Comments

  • Tom Blackwell_2Tom Blackwell_2 Member Posts: 126
    Condenser

    Yes, just use a standard water cooled condenser. Could be shell and coil, tube-in-tube, or plate.
  • NRT_RobNRT_Rob Member Posts: 1,009
    thanks tom

    other than proper sizing, of course, any problems with this?



    I imagine it would be even better than normal, since water offers "buffer capacity" air can't. but I'm making that up.
    Rob Brown
    Designer for Rockport Mechanical
    in beautiful Rockport Maine.
  • Tom Blackwell_2Tom Blackwell_2 Member Posts: 126
    Lift

    The only problem that might be encountered would be a lack of subcooling, resulting in flashing in the liquid line if there is a substantial rise in elevation where the evaporator is located higher than the condenser. As long as the liquid lift is less than 15 feet or so should be ok.
This discussion has been closed.