Leak Loc
Techman
Member Posts: 2,144
I have been using LeakLoc thread sealant for years and just recently my electronic leak detector activated when leak testing a fitting that I had used LeakLoc on.Then I tested the LeakLoc container and my electronic went crazy.Did this happen to anyone else?
0
Comments
-
yes
My leak detector has been doing that for a while, don't know what is in it to cause this but many times while leak checking i forget grab the bubbles trying to pinpoint the leak then i remember that leak loc sets it off. have to look into the reason why tim0 -
Of course it does!
LeakLoc contains Ethanol (Ethyl Alcohol) which is sensed by many electronic leak detectors.0 -
of course
a horse is a horse,OF COURSE ,OF COURSE.Thanks!0