ECM Pumping
NRT_Rob
Member Posts: 1,013
anyone know if the "operate in the middle third of the curve" rule holds true for ECM pumps?
Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.
Designer for Rockport Mechanical
in beautiful Rockport Maine.
0
Comments
-
ECM Pumping
Hi Rob
Short answer is you can select an ECM pump anywhere between min/max head and 0 to max flow without any large loss in efficiency, unlike a constant speed pump where as you have suggested should be selected in the middle 1/3 of it's flow range (to get close to it's BEP).
Typically I select ECM pumps to the right hand side but they rarely run there due to us constantly oversizing pumps and systems.
Hope this helps...0 -
nice
this tech just gets better and better the more I learn about it.Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0 -
ECM Pump Selection - Where on the curve?
Rob, I totally agree - the tech is waaaay cool. As I say in my training classes, 4 innovations in our industry:
1) Electricity
2) Oxygen Barrier (cross link) pipe
3) Condensing Boilers
4) Variable flow ECM pumps
Drop me a line with your mailing address and I will send our our latest traing CD with ECM app drawings (drawn by Siggy) and lots of other info...0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements