High CO levels on Burnham P Series
MacPHJr
Member Posts: 66
in Gas Heating
I am getting a CO Level of 440 ppm in the stack of the boiler. The customer would like to have the house air sealed but the weatherization company wont do it unless the CO levels are below 100 in the stack. How can I lower the CO levels in the stack
0
Comments
-
Lot's to do...
Go here and read this first.
http://www.heatinghelp.com/files/posts/2566/Everything%20You%20Wanted%20to%20Know%20about%20CO....pdf
It's is either too much gas or too little air, or possibly just dirty burners.
METhere was an error rendering this rich post.
0 -
Good Morning Mark:
Nice article. I am what you call a collector of information since reference material is sometimes at a premium. For the young guy's,...Eat this stuff up since it may just save your life or the lives of others. This stuff is free and always a great read. O become an educator and educate the masses.
Again thanks mark for all you do.
Mike T.0 -
No problem Mike
Am here to contribute and help. It's a community of learning.
METhere was an error rendering this rich post.
0 -
First make sure
that you are not over gassed, This can be checked by simply clocking the burner on the test dials on the gas meter.
Next check the inlet and outlet gas pressure to the unit, on most gas valves today this can be done right at the valve.
Insure that the boiler is clean and that there is no blockage.
Make sure the burners are properly aligned and not out of position and impinging on some cooler surface. Pull the burners and clean them.
Is there adequate air for combustion in the combustion zone?
I assume you took other readings with a combustion analyzer, what are they?
Is this equipment flued into a lined masonry chimney or a "B" Vent?
If you give me the input in BTU's and the number of burners I can calculate the orifice size required for you.0 -
Thanks
Hi Tim, I havent been to the site yet. The Co levels were sent to me via email from the energy audit company we are partners with. They do there own testing and when they encounter problems they call us in to make repairs or do service. I will be there tomm and do all of my own testing. I will definitely let you know. Thanks.
Also, i wanted to thank Mark for the article he posted. I actually was with the local fire chief today and he is attending a conference on CO. I dropped off the article in his office and he was going to make copies for all the firefighters. He was very thankful and appreciated the info as did we. Thanks again0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements