need a steam pressure cycle switch
Turbo
Member Posts: 8
I need to replace my steam boiler pressure switch. I have read on this board from a few different threads for a two floor home I should set the switch to .5 psi and the differential to 1 psi. The problem is my boiler keeps going up past those settings to 4 psig and then shuts down. I have changed the gauge with a brand new one to make sure it was not a faulty reading but the gauges are correct. The current pressure switch is a Honeywell but I would like to know if there is something better on the market. A friend of mine bought a brand new Honeywell switch and it was not operating at the correct pressures he set it to. Is there anything better out there?
0
Comments
-
Not just the switch.
Did you clean the pigtail?0 -
Clean
Yes,. The pigtail is clean.0 -
pressuretrol location
some pressuretrols which are tapped into the top of the LWCO can can plug up below the pigtail--could this be the location, and problem with your pressuretrol?
unfortunately, the selection of pressure controls available is limited to the products of only one manufacturer--honeywell. if you decide to replace your pressure control, get a vaporstat [0-16 ounce]. as you continue trying to make your system more comfortable, and quiet, and economical; you will eventually realize that you need one--so why not now?--nbc0 -
Thank You which one do I need?
I was looking at the vaporstat's and there are two with the 0-16oz.
L408J1025 SPST make on pressure rise Only
or
L408J1009 SPDT make R-W, break R-B on pressure rise0 -
another question
I would also like to know why I would not get the 0-4 psi moodels. I noticed the 0-16oz and 0-4psi both are used with a 0-4psi system but have different operating ranges. I am onfused could someone explain please.0 -
Bump for an answer please
Could someone please answer my questions please so I can order the correct vaporstat. Thank you.0 -
0-16oz "1009" Break R-B on Rise
i hadn't seen this thread .. but I think most people here would recommend 0-16oz "1009" Break R-B on Rise1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements