Venting Question
Jeremy_16
Member Posts: 113
I'm trying to calculate how much venting I need. If 3 mains share 11 feet of 4 inch pipe coming up from the header before splitting up, can I
divide the amount of air in that shared part of the mains by 3 so each of
the vents at the end of the 3 mains help vent the air out?
The total cubic feet of air in that shared part of the
main would be .99 cubic feet. If each main needs to vent the air on its
own I would need 1 Gorton #2 (1.1 cfm each) on each of the mains in the
back to vent the air at one ounce of pressure. If they all contribute
to the venting I would only need 1 Gorton#1 (.33 cfm each adding up to the .99 all together) on each back main.
What is suggested in the case of a shared main? Thanks.
divide the amount of air in that shared part of the mains by 3 so each of
the vents at the end of the 3 mains help vent the air out?
The total cubic feet of air in that shared part of the
main would be .99 cubic feet. If each main needs to vent the air on its
own I would need 1 Gorton #2 (1.1 cfm each) on each of the mains in the
back to vent the air at one ounce of pressure. If they all contribute
to the venting I would only need 1 Gorton#1 (.33 cfm each adding up to the .99 all together) on each back main.
What is suggested in the case of a shared main? Thanks.
0
Comments
-
it would seem reasonable
this question in one form or another has come up before without a satisfactory answer AFAIK .. it would seem reasonable to suggest that you can vent the main from the branches .. i might be better if you vented the 11' main as it's own entity and then vented the branches as their own entities... bottom line, as long as you give the air a quick escape route whether by 1 "stairwell" or several .. and as long as the venting of the mains is happening before the venting of the rads... you should be OK .. you never want to make the easiest way out to be by way of the rads.
Of course I'm open to any corrections.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements