Heating Technician

Rach
Member Posts: 1
Steam heat system is making a loud banging noise it is a vacum vapor system with 2 motorized steam valves. Banging seems to be worse when steam valves are closing note this is a residential application. Boiler is 400,000 BTUs operating on a vapor stat with a receiver tank returns are high and dry
I've checked the vacum vapor vents returns and traps they are ok
should I remove vacum vents and leave the system on vapor?
I've checked the vacum vapor vents returns and traps they are ok
should I remove vacum vents and leave the system on vapor?
0
Comments
-
Are those
valves dripped on both sides to the wet returns? If not, they'll be trouble -- and may be your only trouble. Taking the vacuum feature off the vents won't help the banging.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0