Tekmar / caleffi controls for DB
Karl_Northwind
Member Posts: 139
in Solar
Has anyone out here used Tekmar's solar controls? specifically the 155, 156, 157?
I'm going to be installing a large drainback system, and want to do Variable speed circulator for both the primary solar circulator as well as the 2 secondaries that will be sending the heat to the 2 tube and shell HX's for the 2 pools.
Has anyone used the tekmar 157 for variable speed pumping a drainback system?
I'm considering using the Caleffi DB4, but need to run a larger pump than it's relay is rated for.
Hot Rod-- can you give me a hand on spec'ing caleffi controls for this? BTU monitoring as well as control of the solar loop?
thanks
Karl
I'm going to be installing a large drainback system, and want to do Variable speed circulator for both the primary solar circulator as well as the 2 secondaries that will be sending the heat to the 2 tube and shell HX's for the 2 pools.
Has anyone used the tekmar 157 for variable speed pumping a drainback system?
I'm considering using the Caleffi DB4, but need to run a larger pump than it's relay is rated for.
Hot Rod-- can you give me a hand on spec'ing caleffi controls for this? BTU monitoring as well as control of the solar loop?
thanks
Karl
0
Comments
-
new controls
The next batch of Caleffi I-solar controls will all have a drainback function included. So the DB specific controls will go away. The Plus control would be the best choice, some of the middle number controls will be deleted. Two or three should cover all the options.
There will be other changes like a heat dump arr and anti legionella function.
How large of a pump? The control has been tested with a 1.5 amp draw. Tested with a 15-100 Grundfos, Wilo Star 32 and the Taco 0010 on the variable speed triac relay. The fixed speed relay will be a 2 amp.
There is an external relay that Rockwell Automation offers, for controlling a larger draw VS. I have not tried this personally. Rockwell tell us this will work with our control.
The new controls are due any day now. I hope
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
DB controls
I'll either be using a single Taco 1400-45 or equivalent, or 4 taco
009's (one for each array), in which case I'll most likely be using a
single VS control for each circ.
the VS controls will run a
009 right? I like the redundancy, and the fact that i can pick up a 009
anywhere, today. I'll be pumping secondarys to the 2 pools.
I'll leave the specifics of the controls out of the bid till we see what the new stuff is.
thanks
Karl0 -
the control
will switch a 1 amp load on the VS function. The 009 is 1.4 amp at full load, I believe. Un-officially we have run up to a 1.5 amp load on them, but they are listed at 1 amp.
Look for a lower current draw circ or use the iso relay to be safe.
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements