Big picture question
Brian_74
Member Posts: 237
I've realized that I've been asking a lot of detail questions (and you've all been very kind with your replies). I never stopped to ask the bigger question, which is: am I right that I need to replace my traps?
Here's why I thought I need to replace them:
I have 10 traps total. 7 of them are the original Ideal traps from 1929. Three are Trane B-1 traps, which means that they are at least 20 years old. In the LAOSH, Dan explains how the trap elements move a lot in just a few years, and that's why they have relatively short useful lifespans.
There's hammering 6-7 minutes into the 17-20 minute cycles. I thought this might be due to broken traps.
The returns are within 2 degrees of the supplies. I'm not sure this means anything since I would think that both the incoming steam and the outgoing condensate would be 212°F eventually, but I measured it anyway.
I believe that the system is using an excessive amount of gas. It takes 32.5 second to use 2 cu. ft. gas. See <a href="http://www.heatinghelp.com/forum-thread/128784/Under-2-ounces-in2#p1182605">http://www.heatinghelp.com/forum-thread/128784/Under-2-ounces-in2#p1182605</a>
I know that one trap is broken. (<a href="http://www.heatinghelp.com/forum-thread/129166/opening-traps">http://www.heatinghelp.com/forum-thread/129166/opening-traps</a>) I thought that once one breaks, the others are in jeopardy.
So...am I doing the right thing by replacing the trap elements?
Here's why I thought I need to replace them:
I have 10 traps total. 7 of them are the original Ideal traps from 1929. Three are Trane B-1 traps, which means that they are at least 20 years old. In the LAOSH, Dan explains how the trap elements move a lot in just a few years, and that's why they have relatively short useful lifespans.
There's hammering 6-7 minutes into the 17-20 minute cycles. I thought this might be due to broken traps.
The returns are within 2 degrees of the supplies. I'm not sure this means anything since I would think that both the incoming steam and the outgoing condensate would be 212°F eventually, but I measured it anyway.
I believe that the system is using an excessive amount of gas. It takes 32.5 second to use 2 cu. ft. gas. See <a href="http://www.heatinghelp.com/forum-thread/128784/Under-2-ounces-in2#p1182605">http://www.heatinghelp.com/forum-thread/128784/Under-2-ounces-in2#p1182605</a>
I know that one trap is broken. (<a href="http://www.heatinghelp.com/forum-thread/129166/opening-traps">http://www.heatinghelp.com/forum-thread/129166/opening-traps</a>) I thought that once one breaks, the others are in jeopardy.
So...am I doing the right thing by replacing the trap elements?
There was an error rendering this rich post.
0
Comments
-
See my other comment on your other thread...
You may indeed have damaged trap elements; if so, they (obviously) should be replaced. Except for the economic factor, there is no good reason not to replace all of them (except there may be a hassle factor, too). You are quite correct, though, that if one trap is seriously leaking steam, it does threaten the other traps and may shorten their life considerably.
Condensate leaving a trap will approach, but never quite reach, 212 or thereabouts. Very warm condensate is not a problem. However, hot returns may signal a leaking trap. They may also signal excess steam pressure, however.
I can't comment on the gas usage...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Low pressure here
Thanks, Jamie. My boiler doesn't go past 5 ounces/sq. inch on normal runs. When I've had to shut it down for a few hours while doing trap work, it does go as high as 24 oz/si. So I don't think I'm having a pressure problem. On the other hand, I've owned the house for about 10% of its life, so who knows what the other 90% was like.
I mentioned that gas usage in part because I thought that in the LAOSH Dan wrote something like: new traps don't cost you additional money; you're already paying for them in the form of higher fuel bills. (he obviously said it better).
As always, thanks for sharing your knowledge and experience!There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements