Should I?
arcalex
Member Posts: 8
New boiler installed, consulted with local steam guru and installed maximum main vents...I have a mouat system running a pressuretrol set at .5 & 1. Should I install a vaporstat instead? Just trying to see how much more $$ I'll be spending on the system this year.
0
Comments
-
Well...
A vaporstat will give you tighter control of pressure, and lower pressure, than will the pressuretrol -- but you knew that. You also knew, I'm sure, that a Mouat likes really low pressure -- 5 to 8 ounces. That said...
If you are not getting any significant steam in the returns (they may be warm, but should not be hot) and if the system is otherwise working well, a vaporstat might be a waste of money. However, if you are getting any significant steam in any of the returns, the vaporstat will probably manage to pay for itself -- and the system will work better.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
what is...
what is your approx cost/min or cost/hr to run the burner .. then go down and see how many minutes during a cycle you are over a reasonable v-stat setting of ~8oz (when you could be off instead). .. that should help you figure out when/whether the v-stat will be cost effective.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements