Should I?

New boiler installed, consulted with local steam guru and installed maximum main vents...I have a mouat system running a pressuretrol set at .5 & 1. Should I install a vaporstat instead? Just trying to see how much more $$ I'll be spending on the system this year.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,491
    Well...

    A vaporstat will give you tighter control of pressure, and lower pressure, than will the pressuretrol -- but you knew that.  You also knew, I'm sure, that a Mouat likes really low pressure -- 5 to 8 ounces.  That said...



    If you are not getting any significant steam in the returns (they may be warm, but should not be hot) and if the system is otherwise working well, a vaporstat might be a waste of money.  However, if you are getting any significant steam in any of the returns, the vaporstat will probably manage to pay for itself -- and the system will work better.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • jpf321
    jpf321 Member Posts: 1,568
    what is...

    what is your approx cost/min or cost/hr to run the burner .. then go down and see how many minutes during a cycle you are over a reasonable v-stat setting of ~8oz (when you could be off instead). .. that should help you figure out when/whether the v-stat will be cost effective. 
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics