Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Noisy pipe
ansky
Member Posts: 41
I have a 3rd floor bedroom that is heated by a 1-pipe radiator. The steam pipe starts out horizontal in a 2nd floor bedroom (after it comes up from the basement), then runs up a staircase at about a 60-degree angle (very steep staircase), then levels off back to horizontal once it reaches the top of the stairs on the 3rd floor. The problem I have is once the steam reaches the point where it gets to the top of the 3rd floor stairs, I get very noisy hammering for about 30 seconds. What can be done to fix this?
0
Comments
-
The most likely problem
is the pitch of the pipe at the top of the 3rd floor stairs. Make sure that that pipe isn't really horizontal -- it must pitch up towards the radiator at a good 1/2" per foot. So should the one on the second floor.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements