Noisy pipe
ansky
Member Posts: 41
I have a 3rd floor bedroom that is heated by a 1-pipe radiator. The steam pipe starts out horizontal in a 2nd floor bedroom (after it comes up from the basement), then runs up a staircase at about a 60-degree angle (very steep staircase), then levels off back to horizontal once it reaches the top of the stairs on the 3rd floor. The problem I have is once the steam reaches the point where it gets to the top of the 3rd floor stairs, I get very noisy hammering for about 30 seconds. What can be done to fix this?
0
Comments
-
The most likely problem
is the pitch of the pipe at the top of the 3rd floor stairs. Make sure that that pipe isn't really horizontal -- it must pitch up towards the radiator at a good 1/2" per foot. So should the one on the second floor.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0