CPVC Pipe and Snow Melt
LongRunChuck
Member Posts: 1
An owner of a car wash contacted me about hooking up a heat source to his snow melt system already installed in the slabs of the Entrance and Exit Aprons. Owner installed, what he says, is Sch 80 CPVC distribution piping from boiler room out to the 3 sets of remote manifolds. I've never seen CPVC, or PVC for that matter, used in a closed loop water heated system and have a question.
Provided local code permits CPVC piping material in a closed loop heating system, (I'll check before proceeding), is CPVC compatible with a PPG filled system operating at about 130°F? I am thinking 40% PPG / 60% water mix.
Comments?
Provided local code permits CPVC piping material in a closed loop heating system, (I'll check before proceeding), is CPVC compatible with a PPG filled system operating at about 130°F? I am thinking 40% PPG / 60% water mix.
Comments?
0
Comments
-
Non oxygen barrier tube.
PVC, and CPVC are not oxygen barrier tube. However, if you are using all non ferrous components, it shouldn't be an issue.
On the other hand, IF the fluid is being checked annually for pH, and it is maintained above 7.o, but less than 9, you should be OK. The problems arise when the fluid is not properly maintained, and then all ferrous components head south, permanently....
Be careful of who's boiler is used. What you have is essentially an open system.
METhere was an error rendering this rich post.
0 -
correct me if I am wrong....
I really thought that Glycol and CPVC was a No-No... hence the reason that you could not use glycol in Blazemaster sprinkler pipe or else it would eat through it in short order. Glycerin was what I was instructed to use in cpvc.... ty,kpc0 -
Ethylene Glycol is OK
Propylene glycol is so so...
METhere was an error rendering this rich post.
0 -
service tech
I wouldn't do this at all. I have seen several snowmelts (and radiant heat) piped in cpvc. They all failed because of the antifreeze in them. Propylene glycol will attack the pipe and ethylene glycol is poisonous (and probably not code in your area) even if it wouldn't hurt the pipe. Possibly glycerine would work. It has been used in some older solar systems I have seen.0 -
CPVC
I have only dealt with a couple of car washes, both times the owners either installed or modified the systems and both were amazingly screwed up. It must be something in the water or glycol solution but they will spend any amount of time and money rather then pay to have it done right. Good Luck0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements