Thermostat control and Pressure control
Sly
Member Posts: 29
Thermostat control and Pressure controlHow do i prevent the burner from coming back on once a heating cycle is starting.
If the temp has to move from 68 to 71 the boiler builds up steam then cuts off. Then it will come back on in a few minutes because the desired temp is not reached. How can I control this better so it does not keeping running on off so many times before it reaches the desired temp.
thanks
sil
thanks
sil
What are the
settings on your pressuretrol? They should be no more than 2 pounds off to around .5 on.
Is this a new steam boiler or an older one. New boilers make steam fast and have a higher steam velocity so cycling on pressuretrol is not unusual.
Some pictures of your system may help.0 -
yes
The Tekmar 269 control gives outdoor temperature input and uses latent heat. [url=http://www.tekmarcontrols.com/prod/269.shtml]http://www.tekmarcontrols.com/prod/269.shtml
This may do what you want?
I have never installed one but I am sure one of the guys who work on the big systems have used one.Cost is what you spend , value is what you get.
cell # 413-841-6726
Steam Thermostat Cycle rate setting
Hi,
You must also look at the thermostat cycle rate setting. For simple control I would use a Honeywell TH5110D1006 and in the "installer set up" make the change to Heat only and set the cycle rate for steam. Please remember that out of the box it is set for warm air control. This is a +- 1 degree stat and you will not have the temp swing of 68 to 71 degrees which might keep you burner from running on the pressure controller.0 -
THERMOSTAT AND pRESSURE CONTROL
i will upload some photos in a little bit.
thanks
sil0 -
Thermostat control and Pressure control pic
Here are some pics of my system. The lowered the pressure on the two cut in controls. however someone who works on weil mclain boilers said to need to raise both back to 2.5. This way the boiler goes to 5psi then cuts off when the pressure builds. Let me know what you think.0 -
Here are the pics again0
- 125 Chimneys & Flues
