FLOODED BOILER
anthony_12
Member Posts: 9
NEW INSTALLTION OF A NEW STEAM BOILER WITH A M/M WF-2 WATER FEEDER AND A PS-801 LWCO. HARDLY NO RETURNS PIPING DONE TO SPEC.[BURHAM MEGA STEAM].AND THE BOILER FLOODS EVERY 2 DAYS.IT'S A 1-PIPE STEAM SYESTEM W/ALL NEW AIR VENTS.CAN THE BOILER BE GOING INTO A VACUM? WHEN I'M THERE EVERY THING IS OK NO SURGING,LWCO WKS FEEDER WKS.DON'T KNOW WHAT TO DUE NEXT.
0
Comments
-
Flooded Boiler
Hi Anthony- What's the maximum steam pressure reading on the boiler? If should be under two PSI and preferably lower. Does the boiler have DHW coil? Any chance of a bad valve on the water feeder?
- Rod0 -
the great flood
can you turn off the auto fill, and see if you are losing water permanently? water could be "hiding" in a horizontal return close to the waterline and above it. when the pressure returns to zero, then the water comes back. during these temporary low water periods, the auto-fill, can activate, and the end result is over-filling.
you may have some vacuum, if your main vents are inoperative. if so replace and increase that main venting.--nbc0 -
FYI
I'VE REPLACED THE FEEDER ONCE ALREADY.PRESSURETROL SET 1PSI AND NEVER SEEN PRESURE ON THE GAUGE.THERE IS NO COIL ON THE BOILER0 -
TUNED WATER OFF
NO PROBLEM WHEN I LEFT THE FEEDER OFF FOR A COUPLE OF DAYS.THE MAIN VENTS ARE NEW BUT AREN'T THE BEST TYPE LIKE HOFFMANN 75'S.HAVE YOU EVER INSTALLED A HOFFMANN VACUM BREAKER ON A 1 PIPE STEAM SYESTEM? THANKS0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements