Vitodens 200 piping ???
binskibok
Member Posts: 19
in Gas Heating
When looking over the install intructions for the new wb2b 9-26 Vidotens I noted that the boiler supply and returns are 3/4 inch but the LLH is 1 1/4. Should I pipe with 1" (since the indirect TT Smart 40 requires 1") or do I go with 1 1/4 on the boiler side?
0
Comments
-
The Max Flow Rate
Through the boiler is 6.2GPM. Your pipe size needs to be able to carry 6.2GPM to the low loss header. 1" pipe will do the job.There was an error rendering this rich post.
0 -
LLH connections
I'm sure this point has been kicked around before but here goes: In a closed looped hydronic heating system what is the best connection medodology going from the 1" copper to the 1 1/4" male black LLH supplied by Viessmann for piping the Vitodens 200???0 -
Yellow brass fitting...
Neutral to both materials. Accepted by the codes.
METhere was an error rendering this rich post.
0 -
Vitodens 200 Spirovent/Wye strainer/LLH
Vitodens wb2b 9-26 install in a Cape with 3 zones (copper to runtal, black pipe to convectors) using Grunfoss alpha with zone valves. Should a spirotvent and wye strainer be a required part of the system layout or is it a duplication of function using the Low Loss Header. I'm looking for the best efficiency without system redundancy or added costs. Pros or Cons? Your thoughts would be greatly appreciated. THANKS0 -
Brass unions
We have been using brass unions: thread by sweat for the LLH. Binskibok, I also posted on your other thread about the use of a LLH. I also think the insulation is a good touch also.
JeffreyJeffrey Campbell0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements