boiler won't reset

Options
JamesH
JamesH Member Posts: 9
I ran out of oil on my old single pipe steam boiler so I turned off the switch until I got my delivery. After the delivery I turned the switch back on and pushed the reset button and the pump ran for a few seconds and then stopped. I pushed the reset button again and nothing, and the green light on the transformer flashes rather than stay on steady. the instruction on the transformer says if this happens it is locked out and you must push the reset button. pushing the reset does nothing, the light still flashes. Any ideas?

Comments

  • Steamhead
    Steamhead Member Posts: 16,845
    Options
    The fuel unit

    is probably air-bound, and needs to be purged.



    The flashing light is still flashing for a reason. It's telling you to call a pro. Try the Find a Professional page of this site.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • JamesH
    JamesH Member Posts: 9
    Options
    resetting control

    After doing some searching I found my answer on how to reset the Honeywell R7184 series control.

    RESETTING FROM RESTRICTED LOCKOUT

    If the control locks out three times in a row without a complete heat cycle between attempts, the lockout becomes restricted in order to prevent repetitious resetting by the homeowner. To reset, hold down the reset button for 30 seconds (until the LED flashes twice).
  • Leo
    Leo Member Posts: 770
    Options
    Lockout

    Every time I have responded to a call where the homeowner figured out how to reset the control it created a bigger more expensive mess.  Thanks for posting it.



    Leo
  • Jamie Hall
    Jamie Hall Member Posts: 23,327
    Options
    Yep, that's how you do it

    but, unless you are a trained oil burner tech, and know how to correctly purge the fire box and reprime the pump...



    DON"T



    The level of disaster which WILL occur if you don't know exactly what you are doing ranges from badly singed eyebrows to pieces of house all over the neighbourhood.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England