Got a call about a water heater that would not fire up. Nat. Gas had been turned off by gas co.... then turned back on after they payed the bill.
The heater is a std. 35k btu atmosheric set up, nat vent..... pilot will light, stay lit but will not fire. Changed out the gas valve and the t-couple.... stiil have no fire... Gas/ range burner fire up, but the gas dryer also will not fire. I will check pressures in the AM....
Sounds like a meter issue to me but... ???
ty,kpc
The heater is a std. 35k btu atmosheric set up, nat vent..... pilot will light, stay lit but will not fire. Changed out the gas valve and the t-couple.... stiil have no fire... Gas/ range burner fire up, but the gas dryer also will not fire. I will check pressures in the AM....
Sounds like a meter issue to me but... ???
ty,kpc
0
Comments
-
Regulator, air, water?
Gas pressure regulator (just before the meter) often seem to go bad.
Years ago I read the NYC plumbing code book for sometime in the 1800s. It even told how to put in the gas pipes for the gas lights. And how to make illuminating gas from gasoline because not everyone had gas available. Anyhow, if you get air in the gas, the lights can go out for a moment (and of course do not come back on), or worse. Likewise, if the slope on the gas lines is not right, water can collect and the gas has to bubble past the water trap (that should not be there). So you might check these things. None of this is from my direct experience (except gas pressure regulator failures).0 -
Regulator @ the meter
Had this once, similar situation. Pressure will most like show to be fine until the burner from an appliance draws. Check the regulator @ the meter, you could also check the house regulator (2PSI) if you have one.
That sound (uuuummmph!) the regulator makes when you restore flow/pressure through the meter is the regulators diaphragm trying not to get sucked into the house side.
Often this sudden increase can cause that diaphragm to "stick". Check that, although you might not be allowed to touch it.There was an error rendering this rich post.
0 -
Hmmm KCOPP what did you find?
A lot of interesting possibilities offered here, but what did you find when you arrived?0 -
feel dumb... but
I learned something. I did not realize that a orifice that big could clog up....0 -
I hate to sound dumb, but
what orifice? The one in the regulator? Or somewhere else?0 -
burner
Looked as if there was muddy water reside plugging up the burner orifice.... The condensation over the week must have plugged it. Never witnessed that before.
Pressure was 8 " wc... no regulator for the house...low pressure.0 -
Sounds like they might have had
some flooding, if so any equipment which was under water must be replaced for safety reasons.0 -
you would think....
but no... never any flooding. ty,kpc0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements