Pressure testing older gas pipes
Kevin Blair
Member Posts: 62
in Gas Heating
I want to make sure I have done this correctly.
Background info: we have an older home with a solid brick fireplace mantel. The fireplace clearly once held a gas insert of some sort that has long since been removed.
The gas pipe is still there, but has been disconnected in the basement.
We have found a gas stove ( a Bayfield GDS25 from Napoleon) that will fit nicely into the opening and that the sales person tells me will work fine in terms of clearances to combustibles for our situation. The fireplace is on an outer wall and we will direct vent it through the back of the fireplace.
I called the gas company and they told me that the existing pipes are fine as long they pass a pressure test. I have looked up how to do a pressure test and have done it.
Now I want to make sure I didn't miss anything.
The question:
To pressure test the existing pipes I connected a pressure gauge to the pipe outlet at the fireplace.
To the other end (in the basement) I connected my air compressor. I put 30psi into the pipe. The gauge at the compressor reads 30psi. The gauge at the fireplace reads 30psi.
I have left the pressure on for over 2 hours and there has been no movement in either gauge (both read 30psi)...AM I GOOD TO GO??
Thanks,
Kevin
Background info: we have an older home with a solid brick fireplace mantel. The fireplace clearly once held a gas insert of some sort that has long since been removed.
The gas pipe is still there, but has been disconnected in the basement.
We have found a gas stove ( a Bayfield GDS25 from Napoleon) that will fit nicely into the opening and that the sales person tells me will work fine in terms of clearances to combustibles for our situation. The fireplace is on an outer wall and we will direct vent it through the back of the fireplace.
I called the gas company and they told me that the existing pipes are fine as long they pass a pressure test. I have looked up how to do a pressure test and have done it.
Now I want to make sure I didn't miss anything.
The question:
To pressure test the existing pipes I connected a pressure gauge to the pipe outlet at the fireplace.
To the other end (in the basement) I connected my air compressor. I put 30psi into the pipe. The gauge at the compressor reads 30psi. The gauge at the fireplace reads 30psi.
I have left the pressure on for over 2 hours and there has been no movement in either gauge (both read 30psi)...AM I GOOD TO GO??
Thanks,
Kevin
0
Comments
-
I would ask the gas co. or the inspector.
Where I live, they had to pressurize the gas line to 15 psi and it had to hold it for 24 hours. Perhaps they could lose a pound, but not much more. Mine lost something like 9 pounds over the weekend, so they had to fix it.0 -
Pipe Pressure Test
Thanks!
The instructions I found said a minimum of 10 psi for 15 minutes. The instructions were for preparing for an inspection.
I can certainly leave the pressure on for 24 hours or more. I am close to 3 hours w/o the slightest change in pressure.
The gas company told me they would come to check a leak and will not check a disconnected pipe. So I don't think they can help until I have everything installed, not sure about an inspector.0 -
Kevin you are
fine if the pipe held that much pressure it is all set. The gas pressure to the system is only roughly 6 to 7 inches water column about a 1/4 of a pound.
The gas company will not test disconnected pipes and will only come to investigate a leak.
Once permits are pulled and the pipes are connected then your inspector will come and check it and determine if any further tests are required.0 -
Thanks
That's what I was hoping top hear. A few others have said the same thing to me. I actually left the pressure on for 24 hours and both gauges held at 30psi. I will next reconnect the pipe to the gas line. After that I can get the stove and start cutting holes in the wall ;o)0 -
You did cut off the air compressor tank...
... from the gas line, right? Otherwise the volume of the tank would make the leakage less obvious (if there is any).0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements