Anybody replace elements in Marsh 1N traps?
0
Comments
-
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
parts
I have elements for them, but it seems that there should be parts in the body to replace. Is there? TIA, Bryan.0 -
There should be
maybe someone took them out? Not the first time that's happened.......All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
parts
what should find inside them? Haven't had one apart yet. Bryan0 -
Bellows and seat
depending on who made your rebuild parts, the seat may or may not stay in place.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
parts
float and seats. not included in my parts. Number 12 on trap body.0 -
Are these traps
the usual radiator traps, or float-and-thermostatic traps?
Who made the repair kits you bought?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
information
Frank, first of all thanks for the help. These are f and t traps. My supplier ordered elements, Barnes and Jones # 4388. These are the incorrect elements, #1927 is correct. I was able to talk to Tom at Aquatrol-Marsh and he helped me out. Turns out these particular traps are older than anyone knows about. They have a tapping for a bottom outlet, not two side outlets as all the newer ones have. The float mechanism is removed through the top of the trap, but there is a nut that you access through this bottom tap that releases it. I have seven of these traps and two of them are piped using this bottom tap. My problem is this: try to remove the 80 year old piping to access the nut or replace the entire trap which would mean repiping to a trap with a side outlet, again dealing with the old piping. Any ideas? Bryan0 -
If there is a union
in the outlet piping, you should be good to go. If not, this might be a good time to install one. This way you could rebuild the trap without major piping changes. But I'll bet that piping is in better shape than you think.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
unions
Yes, there are unions near the traps. Four of the traps are end of main traps, is that going to make a difference in the quality of the pipe?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements