Weil McLain Series 80 boiler for steam aplication
Gary P
Member Posts: 14
I am in the procces of replaceing a stem boiler in an older shop. It has a Burnham V809 and it has failed due to lack of maintenece. The section failed at the water line. I have always prefered a Burnham boiler ina commercial aplication. My supplyer of choice is a Weil Mclain dealer and I have proposed a Weil McLain eries 80 9 section oil fired with a carlin oil burn Low/high/ low operation. I am looking for opinons on the Series 80 Boiler.
0
Comments
-
We have a couple of 4-80 steamers out there
They work well, though I do wish they were 3-pass rather than pin boilers.
Definitely go with lo-hi-lo. Use a Vaporstat to switch firing rates.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
as with any steam boiler -----you need to find out why the previous 1 failed ---0 -
Weil 80
Great boiler....enough said.
Pay attention to the other posts and find out why the boiler failed.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements