steam radiator
peter petruzzi_2
Member Posts: 4
I have one radiator on the second floor that spits a lot of water out of one radiator. One pipe system, pressure set at about 1 lb. or less. Mains are pitched away from boiler. returns are tied in below water line. Header is 14 in. from water line to bottom of header. Weil Mclane boiler, 1 year old. Scimed boiler many times, added squick, Flush out boiler base and hartford loop regularly. One radiator in kitchen sonds like a pot boiling on a stove. It does not spit water from the vent. System was put in in 1927.Boiler was sized properly. Is header that critical? Worked on high pressure steam,did plumbing,and hot water. these old steam systems are a different Animal!! Thank You
Peter
Peter
0
Comments
-
14 inches?
Yike. Weil-McClain generally specifies 24 inches minimum to the header (check your boiler installation manual). And that assumes that all the oulets are used...
14 inches could produce some serious wet steam problems.
It really is important to regard the manufacturer's piping as minimum requirements to be met.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
or you can
You can post some pictures of the boiler and near pipings for us to help with the problems0 -
pot boiling on a stove
even though your pressuretrol is set to 1 psi, it sounds like you have more pressure than that. you need:
1.a good low pressure gauge [0-15 oz. gaugestore.com]
2.maybe a vaporstat [the standard pressuretrols are VERY inaccurate], and your system will work best under 12 oz.]
3.the downloaded installation manual for your boiler.
4. a copy of "the lost art of steam heating"
how is your venting?--nbc
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements