Steam heat problem

scrook_2
scrook_2 Member Posts: 610
for hot water demand, shut off before it gets to steaming temperatures, say in the 160-190° range, well below the 212-214° range required to produce any steam. Something's amiss -- likely the aquastat, but could be a bum T-stat or something else. It may have been this way awhile, but went unnoticed as T-tsat also called for heat in the colder weather of the winter past and/or hot water use wasn't heavy. Have your service guy check it out.

Comments

  • MASON24
    MASON24 Member Posts: 1


    I have an oil burner that also heats our domestic hot water. It's a steam system and yesterday I noticed a problem. We had some friends over and were getting ready for a big birthday party so about 5 people in a row took showers. Then we noticed how hot the place was getting. I checked the thermostat and it was set for 65 and the temp was 75! And all the radiators were cranking out heat. What's going on here? Is there a valve that should be stopping the steam from getting to the radiators unless the therostat is calling for it? Or is it something else?


    S
  • Jamie Hall
    Jamie Hall Member Posts: 24,648
    and that

    is the downside to having the boiler also do the domestic hot water. Nothing wrong, and the system was doing just what it thought was wanted -- heating the water. What usually happens, though, is that there isn't enough demand for hot water to get the steam really going, and you don't notice it. 5 showers in a row would do it, though...

    The only solution is either separate hot water, or a really big (and insulated) storage tank for the hot water -- that is, of course, if you plan to do this often!

    Or open the windows...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    Maybe

    the aquastat is bad, or set wrong?

    Time to call a pro. Try the Find a Professional page of this site, under Resources at the top of the page.

    "Steamhead"