Steam heat problem
scrook_2
Member Posts: 610
for hot water demand, shut off before it gets to steaming temperatures, say in the 160-190° range, well below the 212-214° range required to produce any steam. Something's amiss -- likely the aquastat, but could be a bum T-stat or something else. It may have been this way awhile, but went unnoticed as T-tsat also called for heat in the colder weather of the winter past and/or hot water use wasn't heavy. Have your service guy check it out.
0
Comments
-
I have an oil burner that also heats our domestic hot water. It's a steam system and yesterday I noticed a problem. We had some friends over and were getting ready for a big birthday party so about 5 people in a row took showers. Then we noticed how hot the place was getting. I checked the thermostat and it was set for 65 and the temp was 75! And all the radiators were cranking out heat. What's going on here? Is there a valve that should be stopping the steam from getting to the radiators unless the therostat is calling for it? Or is it something else?
S0 -
and that
is the downside to having the boiler also do the domestic hot water. Nothing wrong, and the system was doing just what it thought was wanted -- heating the water. What usually happens, though, is that there isn't enough demand for hot water to get the steam really going, and you don't notice it. 5 showers in a row would do it, though...
The only solution is either separate hot water, or a really big (and insulated) storage tank for the hot water -- that is, of course, if you plan to do this often!
Or open the windows...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Maybe
the aquastat is bad, or set wrong?
Time to call a pro. Try the Find a Professional page of this site, under Resources at the top of the page.
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements