differential wheel
In Dan's book on The Lost Art of Steam Heating he says to set cut in on a steam boiler to 1/2 psi and set the differential wheel to 1 psi. What is this diff wheel and where do I find it on my boiler. Is it the pressure gage?
Dwayne
    Jamie Hall Posts: 27,917
    It's one of the controls
    on the pressuretrol or vapourstat. Some of them are subtractive, some additive. You'll have to look and see which it is.
  • scrook_2
    scrook_2 Posts: 610
    Honeywell P-trol
    If it's a common Honeywell PA404A pressuretrol then there's a wheel under its cover for differential (cut-in) adjustment and a screw adjust on top for cutout pressure. See the last page "settings" of:
    http://customer.honeywell.com/techlit/pdf/PackedLit/60-2341.pdf
    Shut off power to your boiler before removing the cover!
  • in dan's 'we got steam heat',
    he details it on pgs 123-126
    Rem77
  • Dwayne B
    Dwayne B Posts: 2
    Thanks to those who responded. It was under the hood of the pressuretrol and I have set it.