Defective radiator
Bob_121
Member Posts: 22
hi all.
I have a question on my newly installed radiators. They are cast iron radiators purchased from a local plumbing/hardware store.
its about 16 columins and about 2 feet tall.
The unit heats up well and all sections gets hot, but it also cools a lot faster than the smaller radiator.
What can be the cause for this?
Can it be a defective radiator valve that limits the amount of steam into the radiator therefore when the t-stat is satisfied, the unit cools faster due to less steam inside the radiator?
Thanks
I have a question on my newly installed radiators. They are cast iron radiators purchased from a local plumbing/hardware store.
its about 16 columins and about 2 feet tall.
The unit heats up well and all sections gets hot, but it also cools a lot faster than the smaller radiator.
What can be the cause for this?
Can it be a defective radiator valve that limits the amount of steam into the radiator therefore when the t-stat is satisfied, the unit cools faster due to less steam inside the radiator?
Thanks
0
Comments
-
Unlikely...
to be defective -- there isn't much that can go wrong with a hunk of iron!
If all the sections get hot, it's getting enough steam. However...
How heavy is it in comparison to the 'smaller' one? The heavier it is, the longer it will take to heat up -- and cool down. Occurs to me that it may be a lot lighter.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Or
They could have been better designed in convection which would cool them off faster.There was an error rendering this rich post.
0 -
Jamie, that is what puzzles me.
the unit is bigger than my smaller rad but cools down ALOT faster....
and why would the design be better if it cools faster? dont we want it to retain heat when the t-stat is satisfied?
0 -
How about
taking some pics and posting them here, so we can see them?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
My money is on better convection on the taller unit. are you sure they are reaching the same temp? Hot can be 140*F or 220*F. Also the room for the larger unit may have a higher delta T from the rad than the room with the small unit. Do you have the EDR of each unit?Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
where in...
the room is it? is it on a cooler wall or near windows? If there a high degree of heat transfer it will cool down faster.0 -
not necessarily
the retention of heat by a radiator has always been one of the nicer features of cast iron radiators -- whether steam or hydronic. But the objective of the whole exercise is to transfer the heat from the boiler to the room, so one which has better convection may just be doing fine! Big Ed has a good point. So does Steamhead -- some pictures of the old and new might be enlightening.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
no problem, i will take pics tonight and post them.
are there any difference b/w hot water heat radiators and steam heat radiators?
the reason i ask is because the tapping for the radiator vent is at the top of the radiator opposite the supply valve.
Dan's book mentioned that the location should be 3/4 of the way down from top.
if this is indeed a hot water radiator? should i leave it in, the unit is getting hot.
0 -
or...
thinner radiator walls/less mass? Maybe some of both.
1 psi steam is 1 psi steam... so hot is hot (~214°). If it was hot water w/ restricted flow that would be a different story.0 -
a ha
the vent should be lower, could be part of the problem there should be a tapping there. Hot water rads can do both steam and hot water. TRUE steam rads can only do steam... they are not coneccted accross the top.0 -
my new rads looks like these slenderized ones from burham:
http://www.burnham.com/slenderized_radiators.htm
the picture shows the vent tapping on the top opposite the supply valve.
the attached pdf shows two tappings. Dan's book recommends air vent to be toward middle opposite of supply, what is the used of top vent tapping?0 -
air bleeder...
valve on a Hot Water radiator.
For a steam radiator you'd plug it or wouldn't drill and tap it in the first place, and would put the steam air vent about 1/2 to 2/3rds of the way down, opposite end from the steam main connection0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements