Carl your info on the pump pressures is wrong, the pump pressures range from 189-334 psi
21= 189-290
28= 218-334
34= 218-334
for your safety you need a gauge that can handle 1.5x the working pressure.
Sounds like you've chosen the G125, please stop by once in a while and let us know how it's working out for you.0 -
I have seen many EKs in operations
worked on one or two and did an install when I worked for someone else many moons ago. NEVER heard a bad thing about them. Some people JUST don't "get it" never will. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Selection Made
All,
Thank you for your constructive comments, suggestions, side notes, comments and opinions stated here. I have learned a lot and appreciate all the assistance from almost every post.
After a few rounds with several suppliers I did select the G125BE with the ST160 horizontal DHW (due to space issues), valved Grundfos circs, taco zone controller. I was leaning towards the 115 but by the time you add up the pieces it was close to the G125 (within $800) and while the G125 is new I beleive the long term benefits will pay off.
The S2000 while a good system came in about $500 less I felt the best long term (cast vs iron) decision was the Buderus.
The selection of a installer was easy at the end of the day - it was the person that was knowledgable and addressed all the questions in detail, verififed the heat loss, was interested in our business, and finally worked with us to configure the system with the components (like flanged valves etc) and steered us away from pitfalls. The other key aspect was inclusion of a three year coverage on all services and components - warranty and cleanings, though I expect the cleaning to be nominal.
Installation is next week Feb 23 and I will write back with post installation comments and feedback.
Carl
0 -
very good
is he going to install the BFU sensor?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
BFU Sensor
Hi Gary,
No we are not planning on doing the BFU room sensor - is this something that we should do? I have read the manual and if I understand this correctly the BFU "looks" at the room temp and the outside temp then adjusts boiler temp accordingly.
If you can give me some rationale and reason why we need the BFU is is most appreciated.
Carl
0 -
It simply makes a 'constant circulation' zone. You're right, it's seeing the room temp and adjusts accordingly. You normally would use this one your most 'used' zone. The boiler is going to maintain heat, so why not send that heat out to the system?
Some heating guys are baffled by these sensors...don't know why they're incredibly simple.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I know the choice has already been made, I think either would have been a great choice. The Ultimate you are replacing pro-actively sounds like it should have gotten consideration too, please let us all know how much oil you save. I wonder if an Ultimate with an indirect and a Tekmar would be in the same ball park, for about 60% of the cost?0 -
Replacement Update
RE: Peckam - Keeping the Ulitmate (29 Yr Old) boiler would have meant all new piping to install the indirect and I would have replaced the Beckett too as it need a new tube, pump etc so at the end of the day may have saved $3k.
RE: Installation Update: Installed Tues Feb 24 - nice and warm, quiet, very even heat. Amazed at the Logimatic the way it modulates the water temp and the blue flame is very nice technology. The LT160 with the GB125 stacked arrangement is nice looking and compact. Nearly endless hot water now - it looses 8 deg overnight or about a deg per hour which is more than buderus specs indicated but not a big deal. The grundfos 3 spd circs are very quiet and work well on the low setting - we have 3 50' zones in hte house. Run time now at 24 hrs in 5 days - need to tweak the logimatic a bit more, have it set on "single" mode as we are not around weekdays and need to reset some of the times.
Overall very pleased with the selection and operation. Will keep in touch here as this goes and monitoring teh oil consumption and keep updating on the performance.
Thanks again for the tips and advice.
Carl0 -
Post Purge Configuration - Logimatic
All,
The Logimatic indicates a "3 minute post puge" is possible with the standard 2107 control, but nothing is mentioned in the manual or operation instructions.
Can anyone shed some light on how this is configured?
Thanks
0 -
Speaking from experience
I would recommend Buderus. I have the System 2000 EK1 Frontier model and not at all happy with the system. First thing people should know is the "Premier Dealers" recommended by EK have nothing to do with quality installations, they have to do with sales. When I complained about the crappy installation I got from one of their Premier Dealers who contracted out the installation to another company, EK just turned away unconcerned and still recommend that Premier Dealer.
OK, so now I know EK lacks integrity and cares more about making a buck. What about the EK representative who came to my house a few times trying to solve my "air problem"? Well, he was very polite and seemed quite knowledgeable but failed to notice my main circulator pump was installed wrong!
Someone above said EK system is easy to install--nonsense!
The EK system must be installed with the base perfectly level. Sound easy? Of course, but not always done. The dynamic Air vent is supposed to rid the system of air and gurgles. Really? Not in my case. What does EK say? The problem is site specific, meaning, the problem is mine and not theirs. But, they cannot prove anything is wrong on my end.
The Premier Dealer out here who has cerified NATE technicians installs every System 2000 with a Spirovent. Why? I mean, if that dynamic air vent works so well, why would they install a Spirovent on every System 2000? Because they want to prevent an air problem and obviously don't believe the hype about that dynamic air vent.
My only reason for posting is that someone else may discover this thread while trying to make a choice between EK and Buderus. If they read my post and still want the EK, good luck to them!
In very cold weather the System 2000 does not heat up like my old Weil McLain. As for that purging business, not really a big deal in cold weather. Plus, I think it makes the baseboards noisier than my old system did.
My oil company sells both EK and Buderus and recommended Buderus. I didn't buy from them, but I should have listened to them.
One last thing about EK, there was a website where owners of EK posted their problems and dealers among others offered to help. The thread was taken down. I contacted the website and asked why the thread was taken down, and I was told EK made them take it down. I could go on but this is a long post and you can buy whatever you want. I have said my piece and the rest is up to you.0 -
Speaking from experience
I would recommend Buderus. I have the System 2000 EK1 Frontier model
and not at all happy with the system. First thing people should know is
the "Premier Dealers" recommended by EK have nothing to do with quality
installations, they have to do with sales. When I complained about the
crappy installation I got from one of their Premier Dealers who
contracted out the installation to another company, EK just turned away
unconcerned and still recommend that Premier Dealer.
OK, so now I know EK lacks integrity and cares more about making a
buck. What about the EK representative who came to my house a few times
trying to solve my "air problem"? Well, he was very polite and seemed
quite knowledgeable but failed to notice my main circulator pump was
installed wrong!
Someone above said EK system is easy to install--nonsense!
The EK system must be installed with the base perfectly level. Sound
easy? Of course, but not always done. The dynamic Air vent is supposed
to rid the system of air and gurgles. Really? Not in my case. What does
EK say? The problem is site specific, meaning, the problem is mine and
not theirs. But, they cannot prove anything is wrong on my end.
The Premier Dealer out here who has cerified NATE technicians installs
every System 2000 with a Spirovent. Why? I mean, if that dynamic air
vent works so well, why would they install a Spirovent on every System
2000? Because they want to prevent an air problem and obviously don't
believe the hype about that dynamic air vent.
My only reason for posting is that someone else may discover this
thread while trying to make a choice between EK and Buderus. If they
read my post and still want the EK, good luck to them!
In very cold weather the System 2000 does not heat up like my old Weil
McLain. As for that purging business, not really a big deal in cold
weather. Plus, I think it makes the baseboards noisier than my old
system did.
My oil company sells both EK and Buderus and recommended Buderus. I didn't buy from them, but I should have listened to them.
One last thing about EK, there was a website where owners of EK posted
their problems and dealers among others offered to help. The thread was
taken down. I contacted the website and asked why the thread was taken
down, and I was told EK made them take it down. I could go on but this
is a long post and you can buy whatever you want. I have said my piece
and the rest is up to you.0 -
Buderus G125 BE Update Nearly 2 Yrs Later
Well, thought to give a short update on the Buderus G125BE selection and overall performance.
Installation Feb 2009 G125BE 21 (smallest unit) w/LT160 Horz Tank, 3 Grundfos Circ Zones, Taco Zone Control, 1 Grundfos HW loop, Ultra Filter
Feb 2009 to Feb 2010 used 450 Gal Oil - vs 890 and 900 gal two previous seasons
Tracking usage it is burning .64 GPH
Nov. 2010 Total Hrs 1050 Still Burning Blue Flame Changed Ultra Filter one Time
Vacuum/Cleaned Unit 3-4 times over last 2 yrs - still working fine
Most Recent Readings: C75 Comb Analyzer - Original Nozzle and Settings of Air @ 4.5 and Pump Pressure @ 280PSI
Outside Air Temp 48*
Boiler Temp 140
O2% 3.2
CO2 13.3
CO PPM 37
COaf 43
Flue temp 265
Efficiency 89.6
Loss 10.4
Excess Air 18.0
The boiler tech and I took readings over 90% Eff @ 125* and lowest was 89.2 Eff at 165*. Also CO2 was in Buderus spec range at 13.3 in all cases.
What was interesting is these # are better than when brand new! We decided not to change anything at this time.
What are you guys seeing with these units as far as perfomance?
Are we in good shape with these specs after over 1000 hrs operation?
Thanks0 -
You made the right choice
You made the right choice, and now don't look back. You are much better off with the Buderus. I suggested the Buderus in this thread and I have the EK System 2000.
Enjoy!0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements